# **OpenEMS Simulation Configuration Steps**
This guide provides step-by-step instructions for setting up and debugging OpenEMS simulations.
---
## **Step 1: Simulator App**
- **Action**:
- Check `enable`.
- Click `save`.
- **Notes**:
- This will clear all existing configurations. Ensure no critical data is lost before proceeding.
- After clearing, all essential settings must be reconfigured in sequence.
---
## **Step 2: Scheduler (All Alphabetically)**
- **Settings**:
- `ComponentID: scheduler0`
- Check `enable`.
- Click `save`.
- **Functionality**:
- Automatically starts the following core components in alphabetical order:
- `core`
- `ess power`
- `evcs power`
- `Controller Api Websocket`
- `log`
- **No additional configuration required** to ensure basic system functionality.
---
## **Step 3: Controller Debug Log**
- **Settings**:
- `ComponentID: ctrlDebugLog0`
- Check `enable` and `Condensed output`.
- **Functionality**:
- Enables debugging mode with condensed logs for troubleshooting and system analysis.
---
## **Step 4: Simulator DataSource (CSV Predefined)**
Configure three data sources to simulate load, PV generation, and ESS data.
1. **Load Meter Data Source**:
- `ComponentID: datasource0`
- Configuration:
- Check `enable`.
- `Factor: 10000`
- `Time-Delta: -1`
- `Source: h0-summer-weekday-standard-load-profile.csv`
2. **PV Meter Data Source**:
- `ComponentID: datasource1`
- Configuration:
- Check `enable`.
- `Factor: 10000`
- `Time-Delta: -1`
- `Source: h0-summer-weekday-pv-production.csv` or `production2`.
3. **ESS Data Source**:
- `ComponentID: datasource2`
- Configuration:
- Check `enable`.
- `Factor: 10000`
- `Time-Delta: -1`
- `Source: h0-summer-weekday-pv-production2.csv`.
---
## **Step 5: Simulator GridMeter Acting**
- **Settings**:
- `ComponentID: gridmeter0`
- Check `enable`.
- **Functionality**:
- Simulates grid monitoring, providing data on grid power, state, and flow direction.
---
## **Step 6: Simulator EssSinglePhase Reacting**
- **Settings**:
- `ComponentID: ess0`
- `Phase: L1` (single-phase setup; use L2 for two-way or L3 for three-phase setups).
- `Datasource-ID: datasource2`
- `Max Apparent Power [VA]: 10000`
- `Capacity [Wh]: 10000`
- `Initial State of Charge [%]: 30`
- `Grid mode: On_Grid` (enables grid interaction).
- **Functionality**:
- Activates a single-phase ESS to simulate power response.
---
## **Step 7: Controller Ess Balancing**
- **Settings**:
- `ComponentID: ctrlBalancing0`
- Configuration:
- `Energy System ID: ess0` (matches Step 6).
- `Grid Meter ID: gridmeter0` (matches Step 5).
- `Target Grid Setpoint: 10`.
- **Functionality**:
- Controls ESS and grid meter to maintain balanced power flow.
---
## **Step 8: Controller Api Websocket**
- **Check**:
- Ensure WebSocket is enabled.
- **Functionality**:
- Facilitates communication between OpenEMS and the UI.
- The UI will not display system status if WebSocket is disabled.
---
## **Step 9: Simulator Battery**
- **Settings**:
- `ComponentID: bms0`
- Check `enable`.
- Configure parameters:
- `Number of slaves: 1`
- `Discharge min voltage: 44`
- `Charge max voltage: 56`
- `Discharge max current: 50`
- `Charge max current: 50`
- `SOC: 75`
- `SOH: 95`
- `Temperature: 30`
- `Capacity KWh: 50`
- `Voltage: 5`
- `Min cell voltage mv: 3300`.
- **Functionality**:
- Activates the battery simulator with customizable parameters.
---
## **Step 10: Simulator NRCMeter Acting**
- **Settings**:
- `ComponentID: meter0`
- Check `enable`.
- Configuration:
- `Datasource-ID: datasource0`.
- **Functionality**:
- Activates load meter simulation, linked to `datasource0`.
---
## **Step 11: Simulator Production Meter Acting**
- **Settings**:
- `ComponentID: meter1`
- Check `enable`.
- Configuration:
- `Datasource-ID: datasource1`.
- **Functionality**:
- Activates PV meter simulation, linked to `datasource1`.
---
## **Additional Recommendations**
1. **Step-by-Step Validation**:
- Save after adding or modifying each component.
- Use the OpenEMS WebSocket interface to verify component statuses incrementally.
2. **Log Monitoring**:
- Enable debug logs (Step 3) for detailed analysis of system interactions.
3. **Simulation Flexibility**:
- Adjust parameters like battery capacity, power limits, and load curves to better simulate real scenarios.
4. **Advanced Features**:
- Use custom data sources or scripts for extended simulation, e.g.:
- EV charging load simulations.
- Fault condition testing (e.g., disconnections, overload).
By completing the above steps, the simulation system will be ready for testing and validation of complex scenarios.
This guide provides step-by-step instructions for setting up and debugging OpenEMS simulations.
---
## **Step 1: Simulator App**
- **Action**:
- Check `enable`.
- Click `save`.
- **Notes**:
- This will clear all existing configurations. Ensure no critical data is lost before proceeding.
- After clearing, all essential settings must be reconfigured in sequence.
---
## **Step 2: Scheduler (All Alphabetically)**
- **Settings**:
- `ComponentID: scheduler0`
- Check `enable`.
- Click `save`.
- **Functionality**:
- Automatically starts the following core components in alphabetical order:
- `core`
- `ess power`
- `evcs power`
- `Controller Api Websocket`
- `log`
- **No additional configuration required** to ensure basic system functionality.
---
## **Step 3: Controller Debug Log**
- **Settings**:
- `ComponentID: ctrlDebugLog0`
- Check `enable` and `Condensed output`.
- **Functionality**:
- Enables debugging mode with condensed logs for troubleshooting and system analysis.
---
## **Step 4: Simulator DataSource (CSV Predefined)**
Configure three data sources to simulate load, PV generation, and ESS data.
1. **Load Meter Data Source**:
- `ComponentID: datasource0`
- Configuration:
- Check `enable`.
- `Factor: 10000`
- `Time-Delta: -1`
- `Source: h0-summer-weekday-standard-load-profile.csv`
2. **PV Meter Data Source**:
- `ComponentID: datasource1`
- Configuration:
- Check `enable`.
- `Factor: 10000`
- `Time-Delta: -1`
- `Source: h0-summer-weekday-pv-production.csv` or `production2`.
3. **ESS Data Source**:
- `ComponentID: datasource2`
- Configuration:
- Check `enable`.
- `Factor: 10000`
- `Time-Delta: -1`
- `Source: h0-summer-weekday-pv-production2.csv`.
---
## **Step 5: Simulator GridMeter Acting**
- **Settings**:
- `ComponentID: gridmeter0`
- Check `enable`.
- **Functionality**:
- Simulates grid monitoring, providing data on grid power, state, and flow direction.
---
## **Step 6: Simulator EssSinglePhase Reacting**
- **Settings**:
- `ComponentID: ess0`
- `Phase: L1` (single-phase setup; use L2 for two-way or L3 for three-phase setups).
- `Datasource-ID: datasource2`
- `Max Apparent Power [VA]: 10000`
- `Capacity [Wh]: 10000`
- `Initial State of Charge [%]: 30`
- `Grid mode: On_Grid` (enables grid interaction).
- **Functionality**:
- Activates a single-phase ESS to simulate power response.
---
## **Step 7: Controller Ess Balancing**
- **Settings**:
- `ComponentID: ctrlBalancing0`
- Configuration:
- `Energy System ID: ess0` (matches Step 6).
- `Grid Meter ID: gridmeter0` (matches Step 5).
- `Target Grid Setpoint: 10`.
- **Functionality**:
- Controls ESS and grid meter to maintain balanced power flow.
---
## **Step 8: Controller Api Websocket**
- **Check**:
- Ensure WebSocket is enabled.
- **Functionality**:
- Facilitates communication between OpenEMS and the UI.
- The UI will not display system status if WebSocket is disabled.
---
## **Step 9: Simulator Battery**
- **Settings**:
- `ComponentID: bms0`
- Check `enable`.
- Configure parameters:
- `Number of slaves: 1`
- `Discharge min voltage: 44`
- `Charge max voltage: 56`
- `Discharge max current: 50`
- `Charge max current: 50`
- `SOC: 75`
- `SOH: 95`
- `Temperature: 30`
- `Capacity KWh: 50`
- `Voltage: 5`
- `Min cell voltage mv: 3300`.
- **Functionality**:
- Activates the battery simulator with customizable parameters.
---
## **Step 10: Simulator NRCMeter Acting**
- **Settings**:
- `ComponentID: meter0`
- Check `enable`.
- Configuration:
- `Datasource-ID: datasource0`.
- **Functionality**:
- Activates load meter simulation, linked to `datasource0`.
---
## **Step 11: Simulator Production Meter Acting**
- **Settings**:
- `ComponentID: meter1`
- Check `enable`.
- Configuration:
- `Datasource-ID: datasource1`.
- **Functionality**:
- Activates PV meter simulation, linked to `datasource1`.
---
## **Additional Recommendations**
1. **Step-by-Step Validation**:
- Save after adding or modifying each component.
- Use the OpenEMS WebSocket interface to verify component statuses incrementally.
2. **Log Monitoring**:
- Enable debug logs (Step 3) for detailed analysis of system interactions.
3. **Simulation Flexibility**:
- Adjust parameters like battery capacity, power limits, and load curves to better simulate real scenarios.
4. **Advanced Features**:
- Use custom data sources or scripts for extended simulation, e.g.:
- EV charging load simulations.
- Fault condition testing (e.g., disconnections, overload).
By completing the above steps, the simulation system will be ready for testing and validation of complex scenarios.
LeoXu's Signature
Limited Partner of UZ Energy
YouTube: UZ Energy
------------------------------------------------------------------------------------------------------
Renewable Energy & Clean Tech
EcoNode promoter
OpenEMS fans
OpenBMS fans
------------------------------------------------------------------------------------------------------
China丨Singapore丨Germany丨USA
Limited Partner of UZ Energy
YouTube: UZ Energy
------------------------------------------------------------------------------------------------------
Renewable Energy & Clean Tech
EcoNode promoter
OpenEMS fans
OpenBMS fans
------------------------------------------------------------------------------------------------------
China丨Singapore丨Germany丨USA