# **OpenEMS Simulation Configuration Steps**
This guide provides step-by-step instructions for setting up and debugging OpenEMS simulations.
---
## **Step 1: Simulator App**
- **Action**:
- Check `enable`.
- Click `save`.
- **Notes**:
- This will clear all existing configurations. Ensure no critical data is lost before proceeding.
- After clearing, all essential settings must be reconfigured in sequence.
---
## **Step 2: Scheduler (All Alphabetically)**
- **Settings**:
- `ComponentID: scheduler0`
- Check `enable`.
- Click `save`.
- **Functionality**:
- Automatically starts the following core components in alphabetical order:
- `core`
- `ess power`
- `evcs power`
- `Controller Api Websocket`
- `log`
- **No additional configuration required** to ensure basic system functionality.
---
## **Step 3: Controller Debug Log**
- **Settings**:
- `ComponentID: ctrlDebugLog0`
- Check `enable` and `Condensed output`.
- **Functionality**:
- Enables debugging mode with condensed logs for troubleshooting and system analysis.
---
## **Step 4: Simulator DataSource (CSV Predefined)**
Configure three data sources to simulate load, PV generation, and ESS data.
1. **Load Meter Data Source**:
- `ComponentID: datasource0`
- Configuration:
- Check `enable`.
- `Factor: 10000`
- `Time-Delta: -1`
- `Source: h0-summer-weekday-standard-load-profile.csv`
2. **PV Meter Data Source**:
- `ComponentID: datasource1`
- Configuration:
- Check `enable`.
- `Factor: 10000`
- `Time-Delta: -1`
- `Source: h0-summer-weekday-pv-production.csv` or `production2`.
3. **ESS Data Source**:
- `ComponentID: datasource2`
- Configuration:
- Check `enable`.
- `Factor: 10000`
- `Time-Delta: -1`
- `Source: h0-summer-weekday-pv-production2.csv`.
---
## **Step 5: Simulator GridMeter Acting**
- **Settings**:
- `ComponentID: gridmeter0`
- Check `enable`.
- **Functionality**:
- Simulates grid monitoring, providing data on grid power, state, and flow direction.
---
## **Step 6: Simulator EssSinglePhase Reacting**
- **Settings**:
- `ComponentID: ess0`
- `Phase: L1` (single-phase setup; use L2 for two-way or L3 for three-phase setups).
- `Datasource-ID: datasource2`
- `Max Apparent Power [VA]: 10000`
- `Capacity [Wh]: 10000`
- `Initial State of Charge [%]: 30`
- `Grid mode: On_Grid` (enables grid interaction).
- **Functionality**:
- Activates a single-phase ESS to simulate power response.
---
## **Step 7: Controller Ess Balancing**
- **Settings**:
- `ComponentID: ctrlBalancing0`
- Configuration:
- `Energy System ID: ess0` (matches Step 6).
- `Grid Meter ID: gridmeter0` (matches Step 5).
- `Target Grid Setpoint: 10`.
- **Functionality**:
- Controls ESS and grid meter to maintain balanced power flow.
---
## **Step 8: Controller Api Websocket**
- **Check**:
- Ensure WebSocket is enabled.
- **Functionality**:
- Facilitates communication between OpenEMS and the UI.
- The UI will not display system status if WebSocket is disabled.
---
## **Step 9: Simulator Battery**
- **Settings**:
- `ComponentID: bms0`
- Check `enable`.
- Configure parameters:
- `Number of slaves: 1`
- `Discharge min voltage: 44`
- `Charge max voltage: 56`
- `Discharge max current: 50`
- `Charge max current: 50`
- `SOC: 75`
- `SOH: 95`
- `Temperature: 30`
- `Capacity KWh: 50`
- `Voltage: 5`
- `Min cell voltage mv: 3300`.
- **Functionality**:
- Activates the battery simulator with customizable parameters.
---
## **Step 10: Simulator NRCMeter Acting**
- **Settings**:
- `ComponentID: meter0`
- Check `enable`.
- Configuration:
- `Datasource-ID: datasource0`.
- **Functionality**:
- Activates load meter simulation, linked to `datasource0`.
---
## **Step 11: Simulator Production Meter Acting**
- **Settings**:
- `ComponentID: meter1`
- Check `enable`.
- Configuration:
- `Datasource-ID: datasource1`.
- **Functionality**:
- Activates PV meter simulation, linked to `datasource1`.
---
## **Additional Recommendations**
1. **Step-by-Step Validation**:
- Save after adding or modifying each component.
- Use the OpenEMS WebSocket interface to verify component statuses incrementally.
2. **Log Monitoring**:
- Enable debug logs (Step 3) for detailed analysis of system interactions.
3. **Simulation Flexibility**:
- Adjust parameters like battery capacity, power limits, and load curves to better simulate real scenarios.
4. **Advanced Features**:
- Use custom data sources or scripts for extended simulation, e.g.:
- EV charging load simulations.
- Fault condition testing (e.g., disconnections, overload).
By completing the above steps, the simulation system will be ready for testing and validation of complex scenarios.
This guide provides step-by-step instructions for setting up and debugging OpenEMS simulations.
---
## **Step 1: Simulator App**
- **Action**:
- Check `enable`.
- Click `save`.
- **Notes**:
- This will clear all existing configurations. Ensure no critical data is lost before proceeding.
- After clearing, all essential settings must be reconfigured in sequence.
---
## **Step 2: Scheduler (All Alphabetically)**
- **Settings**:
- `ComponentID: scheduler0`
- Check `enable`.
- Click `save`.
- **Functionality**:
- Automatically starts the following core components in alphabetical order:
- `core`
- `ess power`
- `evcs power`
- `Controller Api Websocket`
- `log`
- **No additional configuration required** to ensure basic system functionality.
---
## **Step 3: Controller Debug Log**
- **Settings**:
- `ComponentID: ctrlDebugLog0`
- Check `enable` and `Condensed output`.
- **Functionality**:
- Enables debugging mode with condensed logs for troubleshooting and system analysis.
---
## **Step 4: Simulator DataSource (CSV Predefined)**
Configure three data sources to simulate load, PV generation, and ESS data.
1. **Load Meter Data Source**:
- `ComponentID: datasource0`
- Configuration:
- Check `enable`.
- `Factor: 10000`
- `Time-Delta: -1`
- `Source: h0-summer-weekday-standard-load-profile.csv`
2. **PV Meter Data Source**:
- `ComponentID: datasource1`
- Configuration:
- Check `enable`.
- `Factor: 10000`
- `Time-Delta: -1`
- `Source: h0-summer-weekday-pv-production.csv` or `production2`.
3. **ESS Data Source**:
- `ComponentID: datasource2`
- Configuration:
- Check `enable`.
- `Factor: 10000`
- `Time-Delta: -1`
- `Source: h0-summer-weekday-pv-production2.csv`.
---
## **Step 5: Simulator GridMeter Acting**
- **Settings**:
- `ComponentID: gridmeter0`
- Check `enable`.
- **Functionality**:
- Simulates grid monitoring, providing data on grid power, state, and flow direction.
---
## **Step 6: Simulator EssSinglePhase Reacting**
- **Settings**:
- `ComponentID: ess0`
- `Phase: L1` (single-phase setup; use L2 for two-way or L3 for three-phase setups).
- `Datasource-ID: datasource2`
- `Max Apparent Power [VA]: 10000`
- `Capacity [Wh]: 10000`
- `Initial State of Charge [%]: 30`
- `Grid mode: On_Grid` (enables grid interaction).
- **Functionality**:
- Activates a single-phase ESS to simulate power response.
---
## **Step 7: Controller Ess Balancing**
- **Settings**:
- `ComponentID: ctrlBalancing0`
- Configuration:
- `Energy System ID: ess0` (matches Step 6).
- `Grid Meter ID: gridmeter0` (matches Step 5).
- `Target Grid Setpoint: 10`.
- **Functionality**:
- Controls ESS and grid meter to maintain balanced power flow.
---
## **Step 8: Controller Api Websocket**
- **Check**:
- Ensure WebSocket is enabled.
- **Functionality**:
- Facilitates communication between OpenEMS and the UI.
- The UI will not display system status if WebSocket is disabled.
---
## **Step 9: Simulator Battery**
- **Settings**:
- `ComponentID: bms0`
- Check `enable`.
- Configure parameters:
- `Number of slaves: 1`
- `Discharge min voltage: 44`
- `Charge max voltage: 56`
- `Discharge max current: 50`
- `Charge max current: 50`
- `SOC: 75`
- `SOH: 95`
- `Temperature: 30`
- `Capacity KWh: 50`
- `Voltage: 5`
- `Min cell voltage mv: 3300`.
- **Functionality**:
- Activates the battery simulator with customizable parameters.
---
## **Step 10: Simulator NRCMeter Acting**
- **Settings**:
- `ComponentID: meter0`
- Check `enable`.
- Configuration:
- `Datasource-ID: datasource0`.
- **Functionality**:
- Activates load meter simulation, linked to `datasource0`.
---
## **Step 11: Simulator Production Meter Acting**
- **Settings**:
- `ComponentID: meter1`
- Check `enable`.
- Configuration:
- `Datasource-ID: datasource1`.
- **Functionality**:
- Activates PV meter simulation, linked to `datasource1`.
---
## **Additional Recommendations**
1. **Step-by-Step Validation**:
- Save after adding or modifying each component.
- Use the OpenEMS WebSocket interface to verify component statuses incrementally.
2. **Log Monitoring**:
- Enable debug logs (Step 3) for detailed analysis of system interactions.
3. **Simulation Flexibility**:
- Adjust parameters like battery capacity, power limits, and load curves to better simulate real scenarios.
4. **Advanced Features**:
- Use custom data sources or scripts for extended simulation, e.g.:
- EV charging load simulations.
- Fault condition testing (e.g., disconnections, overload).
By completing the above steps, the simulation system will be ready for testing and validation of complex scenarios.
![[Image: Open-EMS-step-by-step-3.png]](https://i.postimg.cc/QBS98pRY/Open-EMS-step-by-step-3.png)
LeoXu's Signature
Limited Partner of UZ Energy
YouTube: UZ Energy
------------------------------------------------------------------------------------------------------
Renewable Energy & Clean Tech
EcoNode promoter
OpenEMS fans
OpenBMS fans
------------------------------------------------------------------------------------------------------
China丨Singapore丨Germany丨USA
Limited Partner of UZ Energy
YouTube: UZ Energy
------------------------------------------------------------------------------------------------------
Renewable Energy & Clean Tech
EcoNode promoter
OpenEMS fans
OpenBMS fans
------------------------------------------------------------------------------------------------------
China丨Singapore丨Germany丨USA